Is this a 220 breaker?

4.5K views 68 replies 21 participants last post by  kelvancra  
#1 · (Edited by Moderator)
well the new jointer IS 220 but I'm wondering if I was wrong and I do have 220 service. There aren't sockets set up but the wire might be there if this is a 220 breaker Sorry the pic posted sideways

Image
 

Attachments

#2 · (Edited by Moderator)
The two double breakers (one taking up slots 5 & 7, the other in slots 11 & 13) are for 220V. Usually those are for your dryer, stove or air conditioner. If one is not being used for anything, it could certainly be used for your jointer. They're both off in your pic, so I have to wonder what they are supposed to be for.

You also have empty slots, so could add another breaker and run new wire for your jointer it they are in use.
 
#4 ·
Electric panels usually have two parallel rows of tabs that run from the main breaker (or lugs in a sub panel). The breakers have slots that fit over these tabs. A breaker that contacts only one tab is "single pole" and provides 120 volts. A breaker that contacts a tab from each row is "double pole" and provides 240 volts.
 
#5 ·
Looks like a double pole 220v breaker to me. You have two bus bars in the center and that sucker should cross both of them. Did you say bare wires? I'd get an electrician out there to look at all of it.
 
#6 ·
I talked to my electrician friend and bought what I need to make it work. I will need to replace the breaker with a double pole 20 amp but that's no big deal. The existing wires are fine, but just were coiled up in a closet. I noticed that when we first bought the house and turned the breaker off to them. I'll wire them into the outlet I just bought and replace the breaker and I should be good to go.
 
#8 ·
Because the Jointer is rated for 15 amps. According to my friend the electrician you should never oversize your breakers. It risks a panel fire. The 20 will allow it to pull a little extra at startup like they tend to do but be in the proper range.
 
#9 ·
curious how a bigger breaker, with proper gauge wire, and something pulling less on it (the 15amps you mentioned) would risk a panel fire?

With that thinking, you risk panel fires on anything in your house not pulling available amps; lights, your alarm clock, cable box, etc etc.

Unless my logic is flawed, which i'm open to being shown.

Ev
 
#10 ·
I think his point is that the breaker won't trip if the machine pulls more than it is supposed to because some sort of failure. I guess that would be more likely to cause a fire on the machine itself. I probably just misunderstood
 
#11 ·
According to my friend the electrician you should never oversize your breakers. It risks a panel fire.
If the existing 30amp circuits were wired correctly (ie: proper size wire), then downsizing your breaker gives you no benefit at all, and will actually limit future use if you want to plug in something bigger down the road.

The breaker is not there to protect the machine (or whatever you plug into the outlet)... it's there to protect the wires in the wall. Otherwise, like Ev said, you should downsize all those 15A wall outlet circuits that only have a 1 amp desk lamp or .5 amp alarm clock plugged in.

Cheers,
Brad
 
#13 · (Edited by Moderator)
What certification does your electrician have? He should know better as Mr. Unix said.

Hmmm, I don't have much confidence in your 'electrician friend.'

I do RV park electrical setup for the pedestals and also RV electrical work.

At an RV park each pedestal is set up at the main panel with a 50 amp 2P2T breaker. From there it travels to the pedestal where, (normally), there is a 50 amp, 30 amp and 20 amp breaker and receptacle.

Dallas
 
#14 · (Edited by Moderator)
Ok I see your point. To be fair I went back an reread exactly what he said. Here it is verbatim:

Me: My jointer plug says 15 amp and the breaker is 30 so is that ok?

Him: Some people would hook it up . but your wire to your jointer is probably good for 20 amps not a good idea to put it on a 30 amp . never good to over size breaker. fire Hazzard.
 
#15 ·
^ That makes it sound like the wire that was run from the breaker isn't rated for 30amp, so he's suggesting you go down to 20amp to get in the proper range of what the wiring is rated for. I 100% agree if that's the situation. Possible he also meant the power cable for the jointer too, not sure given the context exactly, but either way it sounds like he's suggesting to downsize breaker to get under the safe amperage of the wires in question.
 
#18 ·
I talked to my electrician friend and bought what I need to make it work. I will need to replace the breaker with a double pole 20 amp but that s no big deal. The existing wires are fine, but just were coiled up in a closet. I noticed that when we first bought the house and turned the breaker off to them. I ll wire them into the outlet I just bought and replace the breaker and I should be good to go.

- Shane
Smartest thing you did all week!!
 
#19 ·
The jointer's plug/cord doesn't really come into the equation, so long as you've got the proper wire coming from the breaker box. If it's 10AWG wire, leave the 30amp breaker on there. If it's 12AWG wire, switch the breaker to a 20amp one.
 
#20 ·
One thing that's being missed is what type of outlet is on the 30A circuit. I hope it's a 30A rated outlet, if so then the jointer is not going to plug into it. You can't change the outlet to a 20A outlet without changing the breaker to a 20A. So to keep the 30A outlet you either change the plug on the jointer to 30A or use an adapter, both of which I don't recommend.
 
#22 ·
He s almost certainly going to have to change the plug on the jointer anyway, so he might as well just stick a 30A plug on it to match the breaker/receptacle.

- jonah
He doesn't have to change the plug on the jointer and shouldn't. The correct thing to do is to downsize the breaker to 20A and install the proper 20A outlet to match the factory plug on the jointer.
 
#23 ·
He s almost certainly going to have to change the plug on the jointer anyway, so he might as well just stick a 30A plug on it to match the breaker/receptacle.

- jonah

He doesn t have to change the plug on the jointer and shouldn t. The correct thing to do is to downsize the breaker to 20A and install the proper 20A outlet to match the factory plug on the jointer.

- WhyMe
But, then again, a 20 amp receptacle will not accept anything more than 12 gauge wire.
Also, according to NEC, IIRC, a 30 amp circuit may be carried on a 12 gauge wire if it is less than forty feet. I may be wrong, it has been awhile since I checked the book.
 
#24 ·
He s almost certainly going to have to change the plug on the jointer anyway, so he might as well just stick a 30A plug on it to match the breaker/receptacle.

- jonah

He doesn t have to change the plug on the jointer and shouldn t. The correct thing to do is to downsize the breaker to 20A and install the proper 20A outlet to match the factory plug on the jointer.

- WhyMe
That's a correct thing to do. Another is to match the plug to the existing outlet and to leave the breaker alone. That's also significantly cheaper than buying a new breaker and receptacle.
 
#25 · (Edited by Moderator)
But, then again, a 20 amp receptacle will not accept anything more than 12 gauge wire.
Also, according to NEC, IIRC, a 30 amp circuit may be carried on a 12 gauge wire if it is less than forty feet. I may be wrong, it has been awhile since I checked the book.

- Dallas
#12 pigtails can be used to fit 20A outlet. 30A circuit needs #10. No forty foot or less allowance.